Excellent!  Thank you, Roland.  

Margaret

--- Roland Huggins <[EMAIL PROTECTED]> wrote:

> You need to discuss the issue with the AHJ but go
> armed with some  
> ammo (such as why the 10 ft requirement is there). 
> I did an article  
> for the NFPA Journal in 2004 discussing just this
> issue (a copy is on  
> our web site, link is below).
> 
> http://www.firesprinkler.org/techservices/articles/ 
> ceilingpoketsnfpa04.pdf
> 
> Roland
> 
> On Feb 26, 2008, at 4:02 PM, Margaret Zabel wrote:
> 
> > I have two 4' x 4' skylights separated by 9' of
> > ceiling/structure (located at approx. +13') in a
> 5'
> > wide corridor.  Due to the layout of the skylights
> and
> > one additional obstruction (an architectural
> "bridge"
> > located at approx. +8' to +10'), there will be
> four
> > sprinklers at the ceiling/structure level into
> which
> > the skylights are framed. Two of these sprinklers
> are
> > located between the skylights.  The bridge
> requires
> > one sprinkler below it.  This bridge/obstruction
> will
> > NOT impede heat flow from one skylight to the
> next.
> >
> > Do you see any huge problems if I suggest to the
> AHJ
> > that sprinklers might be omitted from these
> skylights?
> >  If these two sprinklers are not omitted, there
> will
> > be (7) sprinklers protecting the floor area along
> a
> > 32' long corridor.
> >
> > Thank you for your thoughts,
> >
> > Margaret Zabel
> > BFP Fire Protection
> > home office:  510-227-5337
> > [EMAIL PROTECTED]
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
>
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:Sprinklerforum- 
> > [EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to