I have two 4' x 4' skylights separated by 9' of
ceiling/structure (located at approx. +13') in a 5'
wide corridor.  Due to the layout of the skylights and
one additional obstruction (an architectural "bridge"
located at approx. +8' to +10'), there will be four
sprinklers at the ceiling/structure level into which
the skylights are framed. Two of these sprinklers are
located between the skylights.  The bridge requires
one sprinkler below it.  This bridge/obstruction will
NOT impede heat flow from one skylight to the next.  

Do you see any huge problems if I suggest to the AHJ
that sprinklers might be omitted from these skylights?
 If these two sprinklers are not omitted, there will
be (7) sprinklers protecting the floor area along a
32' long corridor.

Thank you for your thoughts,

Margaret Zabel
BFP Fire Protection
home office:  510-227-5337
[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to