Joe,
FWIW I haven't done a Kohl's but my ESFR-25 notes say you will need a
minimum 36"clearance to commodities.
It sounds like you have 2'.
Kurt Kingston
Commercial Fire Protection Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Burtell
Sent: Thursday, February 28, 2008 1:43 PM
To: [email protected]
Subject: Kohl's

Has anyone done a Kohl's store lately? In particular I am interested
what
was done in the storage room. I asked some questions about the storage
and I
get the usual, we've never done that before response. Here is what they
have:
17' to deck
15' of storage, 2' wide solid shelf racks, they are really shelf storage
but
it over the 30" limit due to back to back configuration Class I-V and
Group
A plastics Cartoned, unexpanded

I let them know that due to the solid shelf they will need 1 level of
in-rack sprinklers. They gave a .45/2000 which works fine without solid
shelves. Any opinions?