Just recently we did a Linen's and Things and were told to provide a
.45/2000 throughout but at the last minute we were asked to provide a .60 in
the storage area.  I was lead to believe this came up in a review by the
Mass State Fire Marshalls office.  We had already used specifically listed
sprinklers and had exceeded the requirement but it shows that it is worth
asking.  We did of course charge for an extra as we had bid what had been on
the original plans.

Dave Canham
Fire Systems Solutions  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Friday, February 29, 2008 11:17 AM
To: [email protected]
Subject: RE: Kohl's

Nope, the conveyer is still there.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken Miller
Sent: Thursday, February 28, 2008 3:48 PM
To: [email protected]
Subject: RE: Kohl's

Interesting.... I don't see it mentioned in this thread so I have to
ask; Has Kohl's recently changed their configuration and omitted the
clothing conveyor system (similar to what you see at a dry-cleaners)
that runs above all these shelves/racks?  This configuration just added
to the mix when we had to review the design.

MK
***************************************************** 
 Ken Miller 
 Asst. Fire Protection Engineer 
 Las Vegas Fire & Rescue 
 500 N Casino Center Blvd 
 Las Vegas, Nevada 89101 
 Phone:  702-229-4709   Fax:  385-0718 
 email:  [EMAIL PROTECTED] 
*****************************************************

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis
Mack, SET
Sent: Thursday, February 28, 2008 1:02 PM
To: [email protected]
Subject: RE: Kohl's

Yes, Kohl's does not want heads in those areas.  There are typically 4-6
areas where you will have to put them due to an 18" header that you
can't throw under.  However, outside of that, no heads in those areas.

Our shelves were not back to back, and we were directed by the insurance
company to provide the 0.45 / 2000.  This was all signed off by the AHJ
and everyone involved.  I figure that the insurance guys have to pay for
it if something happens, so they should be pretty set on what they want
/ need. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Thursday, February 28, 2008 1:39 PM
To: [email protected]
Subject: RE: Kohl's

That too, I used carefully spaced extended coverage and avoided
sprinklers inside the light baffles as I recall. 


Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- FPDC
Sent: Thursday, February 28, 2008 2:16 PM
To: [email protected]
Subject: Re: Kohl's

In the last Kohl's I did, the shelves were not back-to-back, so I
considered them as shelves. The trickiest part of that job was the
almost unnoticeable light baffles around the exterior.


At 02:43 PM 2/28/2008, you wrote:
>Has anyone done a Kohl's store lately? In particular I am interested 
>what was done in the storage room. I asked some questions about the 
>storage and I get the usual, we've never done that before response.
>Here is what they
>have:
>17' to deck
>15' of storage, 2' wide solid shelf racks, they are really shelf 
>storage but it over the 30" limit due to back to back configuration 
>Class I-V and Group A plastics Cartoned, unexpanded
>
>I let them know that due to the solid shelf they will need 1 level of 
>in-rack sprinklers. They gave a .45/2000 which works fine without solid

>shelves. Any opinions?
>
>
>
>Joe Burtell, SET, CFPS
>Burtell Fire Protection, Inc.
>[EMAIL PROTECTED]
>www.burtellfire.com
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2909 (20080228) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]