OK, I am convinced, LOL. I didn't really expect to get a knowledgeable
answer, I am impressed. 


Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David Powell
(LES)
Sent: Thursday, February 28, 2008 2:33 PM
To: [email protected]
Subject: RE: BASIC HYDRAULICS

Bill - Having served in a nuclear submarine, I have seen those pressure
changes very clearly, especially in the engine room (the 0.4335 pounds per
foot is a little different in seawater).  You use the pressure change to
determine how deep you are.  The pressure stresses on the hull steel at full
depth are tremendous.  The hull steel is several inches thick compared to
your 200 psi water pipe thickness.  That is why almost all submarines do not
go to the bottom of the sea, except in what I call shallow water!

David
 
David L. Powell
Fire Protection Officer
 
LES
P.O. Box 1789 (all mail)
1305 Avenue I
Eunice, NM 88231
 
Tel:          +01 505 394 6021
Mob:        +01 505 602 0382
Email:      [EMAIL PROTECTED]
Web:        www.nefnm.com
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Thursday, February 28, 2008 12:48 PM
To: [email protected]
Subject: RE: BASIC HYDRAULICS

OK but the sea is an open system what is the water pressure inside the
cooling water piping of the nuclear submarine at the bottom of the sea if
the cooling water pumps churn at say 200 PSI? 


Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Thursday, February 28, 2008 1:11 PM
To: [email protected]
Subject: RE: BASIC HYDRAULICS

Like the pressure at the bottom of the sea.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Thursday, February 28, 2008 1:32 PM
To: [email protected]
Subject: Re: BASIC HYDRAULICS

Elevation still comes into play. It is based on the weight of water, which
is independent of other forces that may create pressure.


At 11:55 AM 2/28/2008, you wrote:
>Someone educate me or re-educate me on basic hydraulics, engineering
not
>necessarily sprinkler hydraulics. I understand the difference between
static
>pressure and residual pressure while flowing some amount and how
gravity
>losses come into play with increasing elevation. However I have the
notion
>that a closed system when pressurized has equal pressure thru the
entire
>system such as when testing a sprinkler system at 200 psi. The pressure
in
>the closed system pumped up to 200 psi is 200 psi throughout regardless
of
>elevation?
>
>Bill Minkel, Designer
>Western States Fire Protection, Dallas
>NFPA Member #2578666
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


DISCLAIMER:
This email transmission is confidential Louisiana Energy Services, L.P and
intended solely for the person or organization to which it is addressed. If
you are not the intended recipient, you must not copy, distribute or
disseminate the information or take any action in reliance of it. Any views
expressed in this message are those of the individual sender, except where
the sender specifically states them to be the views of any organization or
employer. If you have received this message in error, do not open any
attachment but please notify the sender (above) and delete this message from
your system. Please rely on your own virus check, as no responsibility is
taken by the sender for any damage arising out of any bug or virus.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to