Greg,

We've been installing tamper switches on the valves of the lines going to 
the retard chamber as required by NFPA 72 and NFPA 13-2002, 8.16.1.4.2 
I've never seen a valve between the water pressure switch and retard 
chamber.  My interpretation is that 8.16.1.4.3 does not nullify 
8.16.1.4.1. It satisfies it because of the or.    As long as the valve 
w/tamper switch is between the pressure switch and alarm valve or dry pipe 
valve, the engineer should be satisfied.  If you have the NFPA 13-2002 
handbook there is a good exhibit on page 329. The requirement for the 
tamper switch has been in 72 for a long time.
 
I hope that helps.

Regards,

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





Gregg Key <[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
02/28/2008 05:25 PM
Please respond to sprinklerforum

To
[email protected]
cc

Subject
Sorta simple question







Greetings all, After seeing where the basic hydraulic question went I 
have to throw these questions out there .
  How do you interpret NFPA 13 2002 ed.8.16.1.4.1? We have an engineer 
stating that it means adding a valve on top of the retard chamber for 
the pressure switch.
                 8.16.1.4.2?  He wants a tamper switch on it. but I have 
not seen the 
ball valve for the alarm line even sealed . does any one seal or lock 
them?
                 8.16.1.4.3 does this one nullify 8.16.1.4.1? if so does 
it still need 
to meet the requirement of 8.16.1.4.2?

     thanks

[attachment "greggk.vcf" deleted by Jim Roberts/GV/FD/FluorCorp] 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to