5.3 Classes of Standpipe Systems.
5.3.1 Class I Systems. A Class I standpipe system shall provide 2½ in.
(65 mm) hose
connections to supply water for use by fire departments and those
trained in handling heavy fire
streams.
5.3.2 Class II Systems.
5.3.2.1 A Class II standpipe system shall provide 1½ in. (40 mm) hose
stations to supply water
for use primarily by trained personnel or by the fire department
during initial response.
5.3.2.2 A minimum 1 in. (25.4 mm) hose shall be permitted to be used
for hose stations in light
hazard occupancies where investigated and listed for this service and
where approved by the
authority having jurisdiction.
5.3.3 Class III Systems. A Class III standpipe system shall provide 1½
in. (40 mm) hose
stations to supply water for use by trained personnel and 2½ in. (65
mm) hose connections to
supply a larger volume of water for use by fire departments and those
trained in handling heavy
fire streams.
5.3.3.1 A minimum 1 in. (25.4 mm) hose shall be permitted to be used
for hose stations in light
hazard occupancies where investigated and listed for this service and
where approved by the
authority having jurisdiction.
5.3.3.2 Where the building is protected throughout by an approved
automatic sprinkler system,
Class II hose stations for use by trained personnel shall not be
required, subject to the approval
of the authority having jurisdiction, provided that each Class I hose
connection is 2½ in. (65
mm) and is equipped with a 2½ in. × 1½ in. (65 mm × 40 mm) reducer and
a cap attached with
a chain, the 130 ft (39.7 m) travel distance limitation shall not apply.
5.4* Required Type of System.
5.4.1 Class I Standpipe Systems.
5.4.1.1 Class I standpipe systems shall be permitted to be any type
described in Section 5.2 in
buildings not classified as high-rise buildings.
5.4.1.2 Class I standpipe systems in buildings classified as high-
rise buildings shall be
automatic or semiautomatic.
5.4.1.2.1 In buildings classified as high-rise, all required
standpipes shall be automatic or
semiautomatic, including partial height and horizontal standpipes that
serve only a portion or
limited number of floors within the building.
5.4.1.3 Where an existing standpipe system having standpipes with a
minimum diameter of 4
in. (100 mm) is to be utilized to supply a new retrofit sprinkler
system, the water supply
required by Section 7.10 shall not be required to be provided by
automatic or semiautomatic
means, provided that the water supply is adequate to supply the
hydraulic demand of the
sprinkler system in accordance with NFPA 13, Standard for the
Installation of Sprinkler
Systems.
5.4.1.4 Class I standpipe systems shall be wet systems except where
piping is subject to
freezing.
5.4.2 Manual Standpipe Systems. Where a manual standpipe system is
provided, each hose
connection shall be provided with a conspicuous sign that reads
“MANUAL STANDPIPE FOR
FIRE DEPARTMENT USE ONLY.”
5.4.3 Class II and Class III Standpipe Systems. Class II and Class III
standpipe systems shall
be automatic wet systems unless located in a facility where piping is
subject to freezing and
where a fire brigade is trained to operate the system without fire
department intervention, in
which case an automatic dry or semiautomatic dry system shall be
permitted.
On Mar 1, 2008, at 6:20 PM, [EMAIL PROTECTED] wrote:
What are the differences in the classes?
Sent from my Verizon Wireless BlackBerry
-----Original Message-----
From: "Ron Greenman" <[EMAIL PROTECTED]>
Date: Sat, 1 Mar 2008 17:46:46
To:[email protected]
Subject: Re: Dumb Question maybe
Tom,
I know you said in your first post but I've lost that part of the
thread--Is
this a high rise by your jurisdiction's definition. Out this way if
3 plus
stories but under 75' this always works fine. Over 75' and we're
highrise
and the standpipe becomes automatic no matter what class.
On Sat, Mar 1, 2008 at 5:28 PM, Tom Duross <[EMAIL PROTECTED]>
wrote:
I agree Ron but don't think this applies here.
It has sufficient capacity, just a pump that's been sized too small.
6" underground, 6" supply main to (2) 4" standpipes, wtf.
Sorry Campers, but this really bothered me. (Not nearly like the
Superbowl
though..)
It's the second system like this I've been asked to test in the
past year.
I mentioned it to the Inspectors but it fell on deaf ears.
Tom
Tom,
NFPA 14, 2007
5.2.5* Manual Wet. A manual wet standpipe system shall be a wet
standpipe system connected to a small water supply for the purpose
of
maintaining water within the system or sharing a water supply with an
automatic sprinkler system, but not having a water supply capable of
delivering the system demand attached to the system.
On 3/1/08, Tom Duross <[EMAIL PROTECTED]> wrote:
Tom,
The Mass Code is confusing on this issue. Section 914.1 states that
when standpipes are required to be installed, they shall be
automatic
wet type. This would mean that they would need to meet the flow and
pressure demands with the on site supply. However, section 914.3
Exception states that the residual pressures are not required to met
if the building is under 70 feet high, effectively making it a
manual
wet standpipe. I think an interpretation may be in order.
Todd
Todd, I'm very familiar with that section BUT these are not manual
standpipes if they're connected to an automatic water supply. If
they
were
separate, OK I can see the justification but they're not. They're
connected
to the same supply as the sprinklers and the fire (sprinkler)
pump. My
understanding of that section says if I have enough street
pressure to
satisfy the sprinklers, I don't have to install a pump just for the
hose
demand (only class 3 in MA). But, these guys designed and
installed a
fire
pump connected to two combination class 3 standpipes and only
sized it
for
the sprinklers. I don't think that's right.
Tom
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Ron Greenman
...at home
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)