If it's Class III and there are 1-1/2" hose stations, then I would say
the water supply should be automatic and satisfy the demand of  the
Class II connections.  But the standard doesn't do an adequate job of
explaining how to design the water supply if the exception is taken for
fully sprinklered buildings and there aren't any hose stations.   If
it's a Class III that looks like a  Class I with 2-1/2" x 1-1/2"
reducers at the hose connections, then I think you're okay with a
manual-wet system, because those connections are intended to be used by
trained responders.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Parsley
Consulting
Sent: Saturday, March 01, 2008 12:16 PM
To: [email protected]
Subject: Never a dumb question 

Tom,

If these are truly class III standpipes by the definition in NFPA-14,
then
they are required by automatic wet systems unless they're subject to
freezing, per 5.4.3.  I think your conclusions is correct, they've sized
the pump incorrectly if the standpipe isn't dry.  

My only word of caution was your comment that the standpipes aren't
manual if they're connected to an automatic water supply.  Manual wet
standpipes are connected to an automatic water supply, but that supply
isn't capable of providing the demand for standpipes.  Several NFPA-14
references suggest that this could be accomplished by a combined
standpipe
sized and calc'd only for the sprinkler system demand.

Just my thoughts.
Ken Wagoner
San Diego, CA

Tom Duross wrote:
> Todd, I'm very familiar with that section BUT these are not manual
> standpipes if they're connected to an automatic water supply.  If they
were
> separate, OK I can see the justification but they're not.  They're
connected
> to the same supply as the sprinklers and the fire (sprinkler) pump.
My
> understanding of that section says if I have enough street pressure to
> satisfy the sprinklers, I don't have to install a pump just for the
hose
> demand (only class 3 in MA).  But, these guys designed and installed a
fire
> pump connected to two combination class 3 standpipes and only sized it
for
> the sprinklers.  I don't think that's right.
>
> Tom
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to