Tom,

If these are truly class III standpipes by the definition in NFPA-14, then
they are required by automatic wet systems unless they're subject to
freezing, per 5.4.3.  I think your conclusions is correct, they've sized
the pump incorrectly if the standpipe isn't dry.
My only word of caution was your comment that the standpipes aren't
manual if they're connected to an automatic water supply.  Manual wet
standpipes are connected to an automatic water supply, but that supply
isn't capable of providing the demand for standpipes.  Several NFPA-14
references suggest that this could be accomplished by a combined standpipe
sized and calc'd only for the sprinkler system demand.

Just my thoughts.
Ken Wagoner
San Diego, CA

Tom Duross wrote:
Todd, I'm very familiar with that section BUT these are not manual
standpipes if they're connected to an automatic water supply.  If they were
separate, OK I can see the justification but they're not.  They're connected
to the same supply as the sprinklers and the fire (sprinkler) pump.  My
understanding of that section says if I have enough street pressure to
satisfy the sprinklers, I don't have to install a pump just for the hose
demand (only class 3 in MA).  But, these guys designed and installed a fire
pump connected to two combination class 3 standpipes and only sized it for
the sprinklers.  I don't think that's right.

Tom
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to