No, 2 1/2" angle valves with 1 1/2" reducers.
5 sty., 56' sidewalk to parapet Steve.
Mixed use.


Tom:

Does the building have 1-1/2" hose stations or not?  I don't mean to
over-simplify, but if not, a wet-manual Class I system is acceptable
unless the local (or state) building code calls for something more.  The
pump sized for the sprinklers is okay so long as the path from the FDC
to the remote outlets calc's out based on whatever inlet pressure the
responding fire department specifies.

Steve Leyton
Protection Design & Consulting

The foregoing is my opinion only and is not intended to represent the
Technical Committee on Standpipe Systems, nor serve as an interpretation
of NFPA 14.