Allow me to repeat what I think you said (why does that make me think of the current commercial where someone is interviewing for a job with a stain on his shirt and everything sounds like gibberish)

You have a pony wall and someone wants to install a sidewall sprinkler at the end of the pony wall (the 6 inch wide part that is parallel with the wall containing the other sidewall sprinklers). I think you could do it BUT the area of coverage along the wall is limited to 6 inches. The only thing that comes close is the criteria for distance off the wall. One also has to take the step that this is a plane throughout the area of coverage (that philosophy is defined under pendent sprinklers). There is also the 8 inch maximum soffit width so we get adequate throw back to cover the floor behind the deflector. Is the pony wall deeper than 8 inches?

WIth heat having to cross the ceiling AND come down the walls to reach the sprinkler, what other conclusion could be drawn. The criteria addresses TWO parameters: not just covering the floor but also activation.

Roland

On Apr 2, 2008, at 2:27 PM, Todd Williams - FPDC wrote:

I am working on a project where a 6" wide wall extends out part way into the space. Piping in this space is to be exposed, so the contractor wants to wrap the pipe around this partition wall and install sidewall sprinklers. In order to do that, he proposes to install a sidewall sprinkler backed up to the end of the 6" end of the wall. I don't think this will work, but he says "where does it say in NFPA 13 that you can't". I can't find anything specific. Anybody else run into this and have any ideas? Am I missing something?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to