Roland, if I understand you correctly, because that head is installed on
a wall 6 inches wide wall it will only correctly throw a path 16ft long
by 6in wide (for 16'x16' sprinkler)? Why? 
Thanks,
Dewayne 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, April 02, 2008 5:40 PM
To: [email protected]
Subject: Re: sidewalls on the end wall

Allow me to repeat what I think you said (why does that make me think of
the current commercial where someone is interviewing for a job with a
stain on his shirt and everything sounds like gibberish)

You have a pony wall and someone wants to install a sidewall sprinkler
at the end of the pony wall (the 6 inch wide part that is parallel with
the wall containing the other sidewall sprinklers).  I think you could
do it BUT the area of coverage along the wall is limited to 6 inches.
The only thing that comes close is the criteria for distance off the
wall.  One also has to take the step that this is a plane throughout the
area of coverage (that philosophy is defined under pendent sprinklers).
There is also the 8 inch maximum soffit width so we get adequate throw
back to cover the floor behind the deflector.  Is the pony wall deeper
than 8 inches?

WIth heat having to cross the ceiling AND come down the walls to reach
the sprinkler, what other conclusion could be drawn.  The criteria
addresses TWO parameters: not just covering the floor but also
activation.

Roland

On Apr 2, 2008, at 2:27 PM, Todd Williams - FPDC wrote:

> I am working on a project where a 6" wide wall extends out part way 
> into the space. Piping in this space is to be exposed, so the 
> contractor wants to wrap the pipe around this partition wall and 
> install sidewall sprinklers. In order to do that, he proposes to 
> install a sidewall sprinkler backed up to the end of the 6" end of the

> wall. I don't think this will work,  but he says "where does it say in

> NFPA 13 that you can't". I can't find anything specific.
> Anybody else run into this and have any ideas? Am I missing something?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080  _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
> field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to