The room (actually a stairway up and down with a building entrance at the intermediate landing) is 17 x 16 and the pony wall sticks out 9 feet. The contractors proposal is to run pipe along one side of he pony wall, wrap around the 6" end and run back the other side. The sprinkler on the end would be the one in question. My take is that it may not activate, but I would like to have something to back me up (or prove me wrong)

At 06:40 PM 4/2/2008, you wrote:
Allow me to repeat what I think you said (why does that make me think
of the current commercial where someone is interviewing for a job
with a stain on his shirt and everything sounds like gibberish)

You have a pony wall and someone wants to install a sidewall
sprinkler at the end of the pony wall (the 6 inch wide part that is
parallel with the wall containing the other sidewall sprinklers).  I
think you could do it BUT the area of coverage along the wall is
limited to 6 inches.  The only thing that comes close is the criteria
for distance off the wall.  One also has to take the step that this
is a plane throughout the area of coverage (that philosophy is
defined under pendent sprinklers).  There is also the 8 inch maximum
soffit width so we get adequate throw back to cover the floor behind
the deflector.  Is the pony wall deeper than 8 inches?

WIth heat having to cross the ceiling AND come down the walls to
reach the sprinkler, what other conclusion could be drawn.  The
criteria addresses TWO parameters: not just covering the floor but
also activation.

Roland

On Apr 2, 2008, at 2:27 PM, Todd Williams - FPDC wrote:

I am working on a project where a 6" wide wall extends out part way
into the space. Piping in this space is to be exposed, so the
contractor wants to wrap the pipe around this partition wall and
install sidewall sprinklers. In order to do that, he proposes to
install a sidewall sprinkler backed up to the end of the 6" end of
the wall. I don't think this will work,  but he says "where does it
say in NFPA 13 that you can't". I can't find anything specific.
Anybody else run into this and have any ideas? Am I missing something?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to