Brian,

A 25% drop is way too much for normal water degradation.  Has anyone talked
with the local water purveyors to see if they have something shut down for
maintenance or something?

I would try that path before going too much further.

Cliff

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Monday, April 07, 2008 1:31 PM
To: [email protected]
Subject: Failed Bucket Test

Fellow forum people:
I have a situation where we have designed and installed a 13R system, it is
completely finished and wham-o we fail the bucket test! Our system was
designed based on the flow test provided by the city fire dept., turns out
that a test taken now with the failed test shows a 25% drop in static &
residual pressures, hence the failed test. Of course the owner is looking to
us to pull a magic rabbit out of our #$% , err I mean hat, we have tried a
few different things but with that big of a pressure loss there's really not
much we can do. I don't feel it's our liability at this point since we went
off the city's water flow test and per the calc's we were good, any
thoughts?
 

Regards,

 
<http://www.firstdefensefire.com/>  

 

 




E-mail message checked by Spyware Doctor (5.5.0.178)
Database version: 5.09560
http://www.pctools.com/spyware-doctor/

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to