Do you mean 13D? Haven't seen any 13R requiring a bucket test. Assuming 13D,
the cheapest solution may be a small pump. Doesn't have to be a listed fire
pump.

The city in my end of the world always adds a disclaimer saying they are not
responsible for the accuracy of the flow test and it should not be relied
on, or something to that effect. 

Good luck,

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: April 7, 2008 12:31 PM
To: [email protected]
Subject: Failed Bucket Test

Fellow forum people:
I have a situation where we have designed and installed a 13R system, it is
completely finished and wham-o we fail the bucket test! Our system was
designed based on the flow test provided by the city fire dept., turns out
that a test taken now with the failed test shows a 25% drop in static &
residual pressures, hence the failed test. Of course the owner is looking to
us to pull a magic rabbit out of our #$% , err I mean hat, we have tried a
few different things but with that big of a pressure loss there's really not
much we can do. I don't feel it's our liability at this point since we went
off the city's water flow test and per the calc's we were good, any
thoughts?
 

Regards,

 
<http://www.firstdefensefire.com/>  

 

 




E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09560 http://www.pctools.com/spyware-doctor/

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to