Brian:
Are you a 4 head design or do you have areas of 13 to calc?
A booster pump approved by the AHJ may be the cheapest alternative, if you
have a lot of 13 area to deal with.(I'm assuming that the 4head residential
calc is not where your short, if it is the 4 head area can you change the
heads to ones with larger orifices?) I know that TALCO has a packaged 13R
fire pump that conforms to NFPA 20 for up to 500 GPM
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Brian Harris" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, April 07, 2008 1:05 PM
Subject: RE: Failed Bucket Test
The city the job is in will not let anybody but the Fire Dept. run the
test.
Brian Harris
FDFP INC.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff Hewitt
Sent: Monday, April 07, 2008 3:02 PM
To: [email protected]
Subject: Re: Failed Bucket Test
Brian,
Just curious...
What were the circumstances that led you to use a test conducted by the
Fire
Department? Are there conservation limitations imposed or something like
that? Why would you not have performed your own test?
Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer
Bi-State
Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by
one
or more legal privileges. It is intended solely for the use of the
addressee identified above. If you are not the intended recipient, any
use,
disclosure, copying or distribution of this e-mail is unauthorized. If
you
received this e-mail in error, please notify the sender immediately at the
above captioned address.
----- Original Message -----
From: "Brian Harris" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, April 07, 2008 1:51 PM
Subject: RE: Failed Bucket Test
Chuck,
Yeah that was one of the first things we did, we also had the local
Utility Dept. go out and check and they found nothing.
Brian Harris
FDFP INC.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chuck
Bowman
Sent: Monday, April 07, 2008 2:42 PM
To: [email protected]
Subject: RE: Failed Bucket Test
Brian,
Has anyone checked to make sure all the valves are fully open, just a
suggestion.
Chuck
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Monday, April 07, 2008 2:31 PM
To: [email protected]
Subject: Failed Bucket Test
Fellow forum people:
I have a situation where we have designed and installed a 13R system, it
is
completely finished and wham-o we fail the bucket test! Our system was
designed based on the flow test provided by the city fire dept., turns
out
that a test taken now with the failed test shows a 25% drop in static &
residual pressures, hence the failed test. Of course the owner is looking
to
us to pull a magic rabbit out of our #$% , err I mean hat, we have tried
a
few different things but with that big of a pressure loss there's really
not
much we can do. I don't feel it's our liability at this point since we
went
off the city's water flow test and per the calc's we were good, any
thoughts?
Regards,
<http://www.firstdefensefire.com/>
E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09560 http://www.pctools.com/spyware-doctor/
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09560 http://www.pctools.com/spyware-doctor/
E-mail message checked by Spyware Doctor (5.5.0.178)
Database version: 5.09560
http://www.pctools.com/spyware-doctor/
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
E-mail message checked by Spyware Doctor (5.5.0.178)
Database version: 5.09560
http://www.pctools.com/spyware-doctor/
E-mail message checked by Spyware Doctor (5.5.0.178)
Database version: 5.09560
http://www.pctools.com/spyware-doctor/
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)