Interestingly our procedures were changed to REQUIRE that the design
engineer perform the test, a representative of our office merely
provides the water maps and observes the test. It is up to the engineer
to choose the hydrants and conduct the test in accordance with 291.
Frankly since the engineer is responsible for the design its only right
that he/she perform the test.

John Drucker  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: Monday, April 07, 2008 3:33 PM
To: [email protected]
Subject: Re: Failed Bucket Test

That's common practice around here Jeff........  One municipality allows
you to read the gauge but not touch anything, most others either the
fire or water department provides the data as requested.

Mind saying what the static is and was?  Have you retried the calcs with
the new flow data?  Do they show changing out the lead-in could solve
the problem?

Garth

----- Original Message -----
From: "Jeff Hewitt" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, April 07, 2008 2:01 PM
Subject: Re: Failed Bucket Test


> Brian,
>
> Just curious...
>
> What were the circumstances that led you to use a test conducted by
the
Fire
> Department?  Are there conservation limitations imposed or something
like
> that?  Why would you not have performed your own test?
>
> Jeff Hewitt, PE, SET, SFPE (Professional Member)
> Corporate Engineer
> Bi-State Fire Protection Corporation
> 241 Hughes Lane
> St. Charles, MO  63301
> 636-946-0011
> 636-946-5172 (FAX)
>
> This e-mail and any attachments are CONFIDENTIAL and may be protected
by
one
> or more legal privileges.  It is intended solely for the use of the
> addressee identified above.  If you are not the intended recipient,
any
use,
> disclosure, copying or distribution of this e-mail is unauthorized.
If
you
> received this e-mail in error, please notify the sender immediately at
the
> above captioned address.
> ----- Original Message ----- 
> From: "Brian Harris" <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Monday, April 07, 2008 1:51 PM
> Subject: RE: Failed Bucket Test
>
>
> > Chuck,
> > Yeah that was one of the first things we did, we also had the local
> > Utility
> > Dept. go out and check and they found nothing.
> >
> >
> > Brian Harris
> > FDFP INC.
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Chuck
> > Bowman
> > Sent: Monday, April 07, 2008 2:42 PM
> > To: [email protected]
> > Subject: RE: Failed Bucket Test
> >
> > Brian,
> > Has anyone checked to make sure all the valves are fully open, just
a
> > suggestion.
> > Chuck
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Brian
> > Harris
> > Sent: Monday, April 07, 2008 2:31 PM
> > To: [email protected]
> > Subject: Failed Bucket Test
> >
> > Fellow forum people:
> > I have a situation where we have designed and installed a 13R
system, it
> > is
> > completely finished and wham-o we fail the bucket test! Our system
was
> > designed based on the flow test provided by the city fire dept.,
turns
out
> > that a test taken now with the failed test shows a 25% drop in
static &
> > residual pressures, hence the failed test. Of course the owner is
looking
> > to
> > us to pull a magic rabbit out of our #$% , err I mean hat, we have
tried
a
> > few different things but with that big of a pressure loss there's
really
> > not
> > much we can do. I don't feel it's our liability at this point since
we
> > went
> > off the city's water flow test and per the calc's we were good, any
> > thoughts?
> >
> >
> > Regards,
> >
> >
> > <http://www.firstdefensefire.com/>
> >
> >
> >
> >
> >
> >
> >
> >
> > E-mail message checked by Spyware Doctor (5.5.0.178) Database
version:
> > 5.09560 http://www.pctools.com/spyware-doctor/
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
> >
> >
> >
> > E-mail message checked by Spyware Doctor (5.5.0.178) Database
version:
> > 5.09560 http://www.pctools.com/spyware-doctor/
> >
> >
> >
> >
> >
> > E-mail message checked by Spyware Doctor (5.5.0.178)
> > Database version: 5.09560
> > http://www.pctools.com/spyware-doctor/
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to