Sounds like a partially closed valve or less likely a pump. Round here
we have pressure reducing stations that change the volume as demand
changes but the pressure is maintained pretty well flat. If the city has
PRV's in the system they may have reprogrammed them or I have seen where
they connected two formerly separate grids and the flow characteristics
changed significantly. All you can do is talk to the water department
people and double check the valves. It isn't unlike a municipal water
company to say everything is fine without really checking the valves.

If you hit a wall with the water department I would appeal to the fire
department. The FD should take an interest because they may not have
sufficient fire flows available for some existing facilities. Required
fire flows can be as much as 4000 gpm depending on local codes etc...

Good Luck,

Ron Fletcher
Aero Automatic
Phoenix, AZ  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, April 08, 2008 10:35 AM
To: [email protected]
Subject: RE: Failed Bucket Test

Yes, the numbers are from the same hydrant, I was wondering if maybe
there was a pump shut off or cut back because this area was in a drought
last year. The local utility dept. says everything seems o.k. on their
end and that they don't share information with the Fire Dept....... 


Brian Harris
FDFP INC.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, April 08, 2008 11:42 AM
To: [email protected]
Subject: RE: Failed Bucket Test

Are the new numbers from the same hydrants? 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, April 08, 2008 7:22 AM
To: [email protected]
Subject: RE: Failed Bucket Test

The original numbers were S=70 & R=60, the new numbers are S=45 &
R=35.... 


Brian Harris
FDFP INC.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Monday, April 07, 2008 5:11 PM
To: [email protected]
Subject: Re: Failed Bucket Test

Brian,
         What is/was  the water flow numbers?

                                        Gregg




E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09560 http://www.pctools.com/spyware-doctor/





E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09570 http://www.pctools.com/spyware-doctor/
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)





E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09570 http://www.pctools.com/spyware-doctor/





E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09570 http://www.pctools.com/spyware-doctor/
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to