Are the sidewalls within the pocket capable of discharging at the same
rate as the pendants?  If they are not then they do not meet the EH
criteria for the space.  Even if there is a ceiling pocket, it is not
excluded from the criteria set forth for the room.  If the room is based
on an EH design criteria, then the whole room needs to be.   You're not
protecting the ceiling, you're still protecting the space below.

 


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 17, 2008 9:09 AM
To: [email protected]
Subject: Extra Hazard Ceiling Pockets

Forum,

Let me know what you guys think about this situation.

I have a college lab building where the AHJ bumped us up to Extra Hazard
Occupancy in the Basement due to storage of flamabile liquids.  The labs
in the basement have a 3 foot deep ceiling pocket above the experiment
table in the center of the room.  We spaced pendents at extra hazard
spacing throughout the room at the lower ceiling level.  We then added
two sidewall sprinklers in the ceiling pocket itself.  The question as
arisen whether we can use sidewalls because the room is to be designed
at extra hazard.  My therory was that the floor level is protected to
extra hazard from the pendents and the sidewalls are only protecting the
ceiling pock itself and not the room below.  Does anyone agree/disagree
with my reasoning. 


This email is intended for named recipients only.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to