John,

I agree with Mark.  The one thing I would add is that until the last issue
of 13, sidewalls under overhead doors were not specifically addressed and I
still don't think they are "listed" for that application.  It may be a valid
point of discussion for the exception when you are talking with the AHJ.

Cliff Whitfield, SET
Fire Design, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Thursday, April 17, 2008 11:50 AM
To: [email protected]
Subject: RE: Extra Hazard Ceiling Pockets

You seem to be stating that the pendant sprinklers at the lower ceiling
are spaced to cover the entire floor area; the sprinklers in the ceiling
pockets are essentially in place ONLY because the pocket doesn't meet
any of the criteria in NFPA 13 for omitting sprinklers within.  Their
coverage of the floor below over-laps the coverage from the pendants.

Under that scenario, I would argue that the sprinklers in the lower
ceiling should adequately protect the hazard. The sidewalls in the
ceiling pockets with reduce any delay in sprinkler operation due to the
pockets and essentially provide "extra water" to the floor area below.
If your calculations can support full flow of the design area, plus the
sprinklers in the ceiling pockets, it seems that you should be fine.

But this will require buy-in from the AHJ.  The sidewall sprinklers are
still not listed for Extra Hazard. This could result in a ruling against
using the sidewalls for the sole reason that "the standard says so" -
and so it may not matter if the arrangement will work.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 17, 2008 8:09 AM
To: [email protected]
Subject: Extra Hazard Ceiling Pockets

Forum,

Let me know what you guys think about this situation.

I have a college lab building where the AHJ bumped us up to Extra Hazard

Occupancy in the Basement due to storage of flamabile liquids.  The labs

in the basement have a 3 foot deep ceiling pocket above the experiment 
table in the center of the room.  We spaced pendents at extra hazard 
spacing throughout the room at the lower ceiling level.  We then added
two 
sidewall sprinklers in the ceiling pocket itself.  The question as
arisen 
whether we can use sidewalls because the room is to be designed at extra

hazard.  My therory was that the floor level is protected to extra
hazard 
from the pendents and the sidewalls are only protecting the ceiling pock

itself and not the room below.  Does anyone agree/disagree with my 
reasoning. 


This email is intended for named recipients only.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to