Fellow forumites,

I guess I need to back up and expand my comments a little.  When I said that
I agree with Mark, I was trying to say that if what Mark described in his
comments about the head spacing (which none of us know for sure except John)
was accurate, and the pendant heads indeed provided adequate coverage for
the EH occupancy, then I believe that the sidewall heads should not
adversely affect the coverage for the room.

I had envisioned a fairly small room with 4 to 6 heads at the lower ceiling
and the ceiling pocket being something like an 8 x 12 area above the table.
(The problem is, since we don't have a "picture" of what John is describing,
it could be a 3000 sf room with a small ceiling pocket).  If it is similar
to what I envisioned, this seems like a case where 13 can't possibly cover
ever known scenario and some sound engineering judgment needs to be made.
(Which I can't actually do since I am not an engineer and don't play one on
TV).  Maybe someone on the forum with a modeling program could get the
actual layout from John, run a model and let us know what the results are. 

Cliff Whitfield, SET
Fire Design, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 17, 2008 1:11 PM
To: [email protected]
Subject: RE: Extra Hazard Ceiling Pockets

The fire plume knows it is being generated by an EH event and acts
differently when it comes into contact with the sprinkler?  I don't
think so.

So what is the issue when you attempt to use a sidewall for EH?

1.  Failure to respond at all - NO
2.  Responding differently - MAYBE since the ceiling jet flow
characteristics for the sidewall position could be different than the
upight/pendent position.
3.  Delivering too little water - NO, the discharge rate is easily
controlled.
4.  The discharge pattern from a sidewall cannot control an EH fire no
matter how close the sprinkler is or how much water it discharges -
Don't know this answer.
5.  NFPA 13 says no - Definitely YES.
6.  Responding too late because the position of the fire can be farther
from the sidewall sprinkler than any EH 100 sq ft or 130 sq ft spacing -
YES if the basis for the prohibition is the EH fire is liable to grow
too big too fast for the sidewalls to keep up.

I think you would have to show a comparable response and comparable
discharge characteristics between the sidewall position and the ceiling
position.  I don't think you can have an OH design in the middle of the
room and a EH design on the perimeter.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: RE: Extra Hazard Ceiling Pockets
From: "Cliff Whitfield" <[EMAIL PROTECTED]>
Date: Thu, April 17, 2008 1:02 pm
To: <[email protected]>

John,

I agree with Mark. The one thing I would add is that until the last
issue
of 13, sidewalls under overhead doors were not specifically addressed
and I
still don't think they are "listed" for that application. It may be a
valid
point of discussion for the exception when you are talking with the AHJ.

Cliff Whitfield, SET
Fire Design, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Sornsin
Sent: Thursday, April 17, 2008 11:50 AM
To: [email protected]
Subject: RE: Extra Hazard Ceiling Pockets

You seem to be stating that the pendant sprinklers at the lower ceiling
are spaced to cover the entire floor area; the sprinklers in the ceiling
pockets are essentially in place ONLY because the pocket doesn't meet
any of the criteria in NFPA 13 for omitting sprinklers within. Their
coverage of the floor below over-laps the coverage from the pendants.

Under that scenario, I would argue that the sprinklers in the lower
ceiling should adequately protect the hazard. The sidewalls in the
ceiling pockets with reduce any delay in sprinkler operation due to the
pockets and essentially provide "extra water" to the floor area below.
If your calculations can support full flow of the design area, plus the
sprinklers in the ceiling pockets, it seems that you should be fine.

But this will require buy-in from the AHJ. The sidewall sprinklers are
still not listed for Extra Hazard. This could result in a ruling against
using the sidewalls for the sole reason that "the standard says so" -
and so it may not matter if the arrangement will work.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND 
701.280.8591
[EMAIL PROTECTED] 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 17, 2008 8:09 AM
To: [email protected]
Subject: Extra Hazard Ceiling Pockets

Forum,

Let me know what you guys think about this situation.

I have a college lab building where the AHJ bumped us up to Extra Hazard

Occupancy in the Basement due to storage of flamabile liquids. The labs

in the basement have a 3 foot deep ceiling pocket above the experiment 
table in the center of the room. We spaced pendents at extra hazard 
spacing throughout the room at the lower ceiling level. We then added
two 
sidewall sprinklers in the ceiling pocket itself. The question as
arisen 
whether we can use sidewalls because the room is to be designed at extra

hazard. My therory was that the floor level is protected to extra
hazard 
from the pendents and the sidewalls are only protecting the ceiling pock

itself and not the room below. Does anyone agree/disagree with my 
reasoning. 


This email is intended for named recipients only.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to