NFPA 13 in 1989 mentioned protection of Cold rooms.  That's the oldest
version I've got here in the office.  But remember, NFPA 13 doesn't
dictate when it's required, just how to execute it.  Building code
dictates when.   


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Tuesday, May 13, 2008 3:28 PM
To: [email protected]
Subject: Sprinkler heads in coolers/freezers

If I may tap into the collective memory bank of sprinkler knowledge, How
long have sprinklers been required in coolers/freezers per NFPA 13? 
Thanks Gregg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]