Greg, The requirement for sprinklers in coolers and freezers has been in NFPA 13 since before the handbook format started. I recall seeing something prior to the handbook, however the 1983 handbook edition states as a formal interpretation...
Question: Is it the intent of section 4-4 to require sprinkler protection in walk-in type coolers and freezers in fully sprinklered buildings? Answer: Yes. Jack W. Carlson, SET Triple "A" Fire Protection, Inc. [EMAIL PROTECTED] (706) 247-5050 cell -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key Sent: Tuesday, May 13, 2008 3:28 PM To: [email protected] Subject: Sprinkler heads in coolers/freezers If I may tap into the collective memory bank of sprinkler knowledge, How long have sprinklers been required in coolers/freezers per NFPA 13? Thanks Gregg _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)