Greg,

The requirement for sprinklers in coolers and freezers has been in NFPA
13 since before the handbook format started.  I recall seeing something
prior to the handbook, however the 1983 handbook edition states as a
formal interpretation... 

Question:  Is it the intent of section 4-4 to require sprinkler
protection in walk-in type coolers and freezers in fully sprinklered
buildings?

Answer:  Yes. 


Jack W. Carlson, SET
Triple "A" Fire Protection, Inc.
[EMAIL PROTECTED]
(706) 247-5050 cell

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Tuesday, May 13, 2008 3:28 PM
To: [email protected]
Subject: Sprinkler heads in coolers/freezers

If I may tap into the collective memory bank of sprinkler knowledge, How
long have sprinklers been required in coolers/freezers per NFPA 13? 
Thanks Gregg