Subject: RE: Sprinkler heads in coolers/freezers
Greg,
The requirement for sprinklers in coolers and freezers has been in NFPA
13 since before the handbook format started. I recall seeing something
prior to the handbook, however the 1983 handbook edition states as a
formal interpretation...
Question: Is it the intent of section 4-4 to require sprinkler
protection in walk-in type coolers and freezers in fully sprinklered
buildings?
Answer: Yes.
Jack W. Carlson, SET
Triple "A" Fire Protection, Inc.
[EMAIL PROTECTED]
(706) 247-5050 cell
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Tuesday, May 13, 2008 3:28 PM
To: [email protected]
Subject: Sprinkler heads in coolers/freezers
If I may tap into the collective memory bank of sprinkler knowledge, How
long have sprinklers been required in coolers/freezers per NFPA 13?
Thanks Gregg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)