Use a pressure reducing valve and calcs would be in order. Thank you, Greg McGahan
Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key Sent: Wednesday, May 14, 2008 3:08 PM To: [email protected] Subject: Re: Pressure Regulating Valve Maybe a pressure relief valve would work Larrimer, Peter A wrote: > I have a facility in North Carolina who is having pressure > fluctuations in the water supply such that their CPVC systems are > bursting due to overpressures. They have recorded pressures that > easily exceed the 175lb limits of the systems. > > What would the recommendations of the forum be to keep the pressures > down to a reasonable level? (Pressure regulating valve?) > > Will any hydraulics analysis be necessary when any device is installed > in the system? > > Anyone in North Carolina want to contact me concerning this work? > > Thanks in advance. > > Pete Larrimer > VA > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)