Roland reminds me of a military hangar we did with the same problem. A large
expansion tank and a relief valve worked in this situation. In yours;
however, the tank should be smaller but it will be expensive.

Russell


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, May 14, 2008 6:21 PM
To: [email protected]
Subject: Re: Pressure Regulating Valve

You may be looking at it too narrowly (ie looking at the symptom of  
high pressure). In order to get high pressures, you have either (or  
both) thermal expansion which your relief valve will address or  
pressure surges.  If you are getting hammered by a 400 psi spike, a  
relief valve won't help.   Back in my consulting days, we called it a  
transitional pressure wave when we evaluated the Air Force One hangar  
after they had a hydrant act like a missile (a low elevation model).

Roland

PS:  Pete - give me a shout so we can talk about NFPA 25

On May 14, 2008, at 11:54 AM, Larrimer, Peter A wrote:

> I have a facility in North Carolina who is having pressure  
> fluctuations
> in the water supply such that their CPVC systems are bursting due to
> overpressures.  They have recorded pressures that easily exceed the
> 175lb limits of the systems.
>
> What would the recommendations of the forum be to keep the pressures
> down to a reasonable level?  (Pressure regulating valve?)
>
> Will any hydraulics analysis be necessary when any device is installed
> in the system?
>
> Anyone in North Carolina want to contact me concerning this work?
>
> Thanks in advance.
>
> Pete Larrimer
> VA
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.16/1433 - Release Date: 5/14/2008
4:44 PM
 

No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.16/1433 - Release Date: 5/14/2008
4:44 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to