He is nuts.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Monday, June 02, 2008 6:48 AM
To: [email protected]
Subject: RE: 200 psi test for components rated 175

We have one AHJ that won't allow us to touch the check valve after the
200PSI test because we are "altering" the system that has been tested.
He makes all the contractors install a "bypass" around with FDC check
valve and install a butterfly valve in-line to test the BFP without
having to remove the check valve or it's clapper.  Has anyone heard of
this not being allowed in 25 or is the AHJ just making a reach?
Thanks,
Dewayne 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Friday, May 30, 2008 1:58 PM
To: [email protected]
Subject: RE: 200 psi test for components rated 175

Seeing as the backflow isn't a fire appliance, it makes sense that it's
outside the scope of 13.   I'm pretty sure the "full forward flow test"
is a jurisdictional agency thing, i.e. NAVFAC or the serving water
company.   So fire officials might require it too - for peace of mind
perhaps?

BTW, you mitigate the clapper issue by turning the FDC body upside down.
Duh.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Sornsin
Sent: Friday, May 30, 2008 11:33 AM
To: [email protected]
Subject: RE: 200 psi test for components rated 175

Don't most FDCs include clappers?  How do you backwards flow out an FDC
with clappers? And what do you do when the system has a high demand
volume - say over 500 gpm? You'll have a tough time flowing it out an
FDC even without clappers.

Seems it's the responsibility of the engineer of record (when they're
present) to require the test outlet so the owner has a means of meeting
the requirements of NFPA 25 - even if the inspectors never end up
testing the backflow.

When there is not an engineer of record, and a contractor is asked to
design/install a system per code, I don't believe there is any language
in NFPA 13 that would force a contractor to install the test outlet.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc. 
Fargo, ND
701.280.8591
[EMAIL PROTECTED] 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Friday, May 30, 2008 12:23 PM
To: [email protected]
Subject: Re: 200 psi test for components rated 175

Yep, that could be the reason it is shown.

Yea Matt, sorta trick question, We have installed a few wall hydrants at
Military bases.
        Funny thing is that they do there own inspections and they don't
follow NFPA 25 that requires an annual forward flow on the backflows. So
the only systems in our area that do have them , are not being used.
        OK while we are at it, how many NFPA 25 inspectors perform the
required forward flow test annually?


-
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to