The reason for the by-pass is to provide the forward flow for the BFP not the hydro test. He will not let us alter the system by either reversing the check or pulling the clapper and requires the by-pass on all 13 systems. Dewayne
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Monday, June 02, 2008 10:07 AM To: [email protected] Subject: RE: Re[2]: 200 psi test for components rated 175 Am I missing something here? Why not just pump thru the FDC connection, leave the clapper in place and hydro as normal? If the ahj wants the FDC tested with the rest of the system, this is the only way to go. One male NST adapter or One adapter and one plug and your good to go. I can see no advantage to all that extra work. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Coastal Sent: Monday, June 02, 2008 6:48 AM To: Dewayne Martinez Subject: Re[2]: 200 psi test for components rated 175 Hello Dewayne, I know of at least 1 check valve that has a "Test Cap" listed in their parts breakdown. Just the bolt on cover without a clapper (It was in a spec a couple of years ago). We use the CV=1F a lot and I got some replacement covers for the guys to use for testing. Monday, June 2, 2008, 7:48:01 AM, you wrote: > We have one AHJ that won't allow us to touch the check valve after the > 200PSI test because we are "altering" the system that has been tested. > He makes all the contractors install a "bypass" around with FDC check > valve and install a butterfly valve in-line to test the BFP without > having to remove the check valve or it's clapper. Has anyone heard of > this not being allowed in 25 or is the AHJ just making a reach? > Thanks, > Dewayne > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Steve > Leyton > Sent: Friday, May 30, 2008 1:58 PM > To: [email protected] > Subject: RE: 200 psi test for components rated 175 > Seeing as the backflow isn't a fire appliance, it makes sense that it's > outside the scope of 13. I'm pretty sure the "full forward flow test" > is a jurisdictional agency thing, i.e. NAVFAC or the serving water > company. So fire officials might require it too - for peace of mind > perhaps? > BTW, you mitigate the clapper issue by turning the FDC body upside down. > Duh. > Steve Leyton > Protection Design & Consulting > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Mark > Sornsin > Sent: Friday, May 30, 2008 11:33 AM > To: [email protected] > Subject: RE: 200 psi test for components rated 175 > Don't most FDCs include clappers? How do you backwards flow out an > FDC with clappers? And what do you do when the system has a high > demand volume - say over 500 gpm? You'll have a tough time flowing it > out an FDC even without clappers. > Seems it's the responsibility of the engineer of record (when they're > present) to require the test outlet so the owner has a means of > meeting the requirements of NFPA 25 - even if the inspectors never end > up testing the backflow. > When there is not an engineer of record, and a contractor is asked to > design/install a system per code, I don't believe there is any > language in NFPA 13 that would force a contractor to install the test outlet. > Mark A. Sornsin, PE > Fire Protection Engineer > Ulteig Engineers, Inc. > Fargo, ND > 701.280.8591 > [EMAIL PROTECTED] > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Gregg > Key > Sent: Friday, May 30, 2008 12:23 PM > To: [email protected] > Subject: Re: 200 psi test for components rated 175 > Yep, that could be the reason it is shown. > Yea Matt, sorta trick question, We have installed a few wall hydrants > at Military bases. > Funny thing is that they do there own inspections and they > don't follow NFPA 25 that requires an annual forward flow on the > backflows. So the only systems in our area that do have them , are not being used. > OK while we are at it, how many NFPA 25 inspectors perform the > required forward flow test annually? > - > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) -- Best regards, Charles Thurston CET Coastal Fire Protection Coastal mailto:[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)