In the flat lands, you MAY have a 2 in drain that could do full flows up
to OHII - depending on the configuration of the riser and drain line.
But the point of the test is to compare the actual pressure drop through
the backflow with the manufacturer's curve.  So you must accurately
measure the flow.  How does one do that on a typical 2 in drain outlet?

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, May 30, 2008 4:39 PM
To: [email protected]
Subject: RE: Full-flow backflow test

Back to the "Main Drain Test" (Just as a note, most of our systems will
flow
full design, even for OH II thru a 2" main drain connection. If you
install
the main drain you've provided the ability to full forward flow the
backflow
device.) Static Psi over 120 with residual above 100 flowing over 3500
Gpm.
Our normal. Those big hill's called the "Rockies" make reducing pressure
our
problem. A PRV station fails and we increase Psi by more than 50%.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Friday, May 30, 2008 3:26 PM
To: [email protected]
Subject: Re: Full-flow backflow test

Gregg,

I was addressing older systems per NFPA 25 built to a prior code where
there
is no means to test full-flow and no requirement to add such a means.
Even
in these cases you have to forward flow as best you can.



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to