The AHJ is following the example in the annex.

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Dewayne Martinez
----- >Sent: Monday, June 02, 2008 6:48 AM
----- >To: [email protected]
----- >Subject: RE: 200 psi test for components rated 175
----- >
----- >We have one AHJ that won't allow us to touch the check 
----- >valve after the 200PSI test because we are "altering" 
----- >the system that has been tested.
----- >He makes all the contractors install a "bypass" around 
----- >with FDC check valve and install a butterfly valve 
----- >in-line to test the BFP without having to remove the 
----- >check valve or it's clapper.  Has anyone heard of this 
----- >not being allowed in 25 or is the AHJ just making a reach?
----- >Thanks,
----- >Dewayne 
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Steve Leyton
----- >Sent: Friday, May 30, 2008 1:58 PM
----- >To: [email protected]
----- >Subject: RE: 200 psi test for components rated 175
----- >
----- >Seeing as the backflow isn't a fire appliance, it makes 
----- >sense that it's
----- >outside the scope of 13.   I'm pretty sure the "full 
----- >forward flow test"
----- >is a jurisdictional agency thing, i.e. NAVFAC or the 
----- >serving water
----- >company.   So fire officials might require it too - for 
----- >peace of mind
----- >perhaps?
----- >
----- >BTW, you mitigate the clapper issue by turning the FDC 
----- >body upside down.
----- >Duh.
----- >
----- >Steve Leyton
----- >Protection Design & Consulting
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Mark Sornsin
----- >Sent: Friday, May 30, 2008 11:33 AM
----- >To: [email protected]
----- >Subject: RE: 200 psi test for components rated 175
----- >
----- >Don't most FDCs include clappers?  How do you backwards 
----- >flow out an FDC with clappers? And what do you do when 
----- >the system has a high demand volume - say over 500 gpm? 
----- >You'll have a tough time flowing it out an FDC even 
----- >without clappers.
----- >
----- >Seems it's the responsibility of the engineer of record 
----- >(when they're
----- >present) to require the test outlet so the owner has a 
----- >means of meeting the requirements of NFPA 25 - even if 
----- >the inspectors never end up testing the backflow.
----- >
----- >When there is not an engineer of record, and a 
----- >contractor is asked to design/install a system per code, 
----- >I don't believe there is any language in NFPA 13 that 
----- >would force a contractor to install the test outlet.
----- >
----- >Mark A. Sornsin, PE
----- >Fire Protection Engineer
----- >Ulteig Engineers, Inc. 
----- >Fargo, ND
----- >701.280.8591
----- >[EMAIL PROTECTED] 
----- > 
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Gregg Key
----- >Sent: Friday, May 30, 2008 12:23 PM
----- >To: [email protected]
----- >Subject: Re: 200 psi test for components rated 175
----- >
----- >Yep, that could be the reason it is shown.
----- >
----- >Yea Matt, sorta trick question, We have installed a few 
----- >wall hydrants at Military bases.
----- > Funny thing is that they do there own inspections and 
----- >they don't follow NFPA 25 that requires an annual 
----- >forward flow on the backflows. So the only systems in 
----- >our area that do have them , are not being used.
----- > OK while we are at it, how many NFPA 25 inspectors 
----- >perform the required forward flow test annually?
----- >
----- >
----- >-
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to