Im not sure where in the 2007 edition since we are only using the 2002 edition 
but here's how and when I see or require them in projects:
In a project where there is concealed combustible construction such as truss 
voids and intersistal spaces when the building requires full NFPA 13 protection 
(versus 13R & 13D) then they use the CC heads and follow the spacing and design 
criteria of the manufacturer.  Often times this 'full' coverage comes about in 
buildings otherwise under the 13D or 13R standards but due to height & area 
increases (modifications as otherwise known) the building is required to have 
full NFPA 13 coverage. 
There also have been some recent changes to the listing information for CPVC 
piping when run in concealed combustible spaces that require sprinkler 
protection that you MUST use a listed specific application concealed 
combustible head.  Occasionally concealed combustible spaces are protected with 
SSU or even SSP heads but that is no longer permissible when using CPVC piping.
I guess my answer is that most often times the building code which drives the 
actual sprinkler requirement will indicate what level of protection is required 
(13, 13R or 13D) and from there you follow the standard for where and what gets 
protected.
Simple case in point is a residential building 4 stories of wood frame 
construction.  this would seem to be a 13R building and therefore exempt the 
attic of sprinkler protection.  If the design professional has elected to take 
the area modification to build larger per floor than the building code permits 
(Table 503) then the sprinkler protection must be in accordance with NFPA 13 
and now we suddenly see a suppressed attic and concealed combustible spaces 
...... truss voids or intersistal floor spaces if they cant make any of the 
exemptions in NFPA 13 8.14.1 of the 2002 edition.
Just one of many possible examples.
Dave P.
An AHJ in NJ