This requirement is only for 2007, am I correct?

I've 2 other questions.

(1) Tyco cut sheets state this head is used for light hazard. If the area is
OH what happens? Sometimes a crawlspace is used as a mechanical room, with
tanks, pumps and other mechanical equipment.

(2) Sometimes a crawlspace is non-combustible with drywall attached to
bottom of wood joists or TJI's, but is required to be sprinklered due to
storage/mech. equipment etc. I would think 8.15.1.6 (07) should apply, but
is the wording clear? In this case, I think the 36" clearance is from floor
to ceiling (bottom of drywall) of the crawlspace. Right?

Tony 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt Willis
Sent: July 28, 2008 7:33 AM
To: [email protected]
Subject: FW: CC sprinklers

 

-----Original Message-----
From: Matt Willis
Sent: Monday, July 28, 2008 8:30 AM
To: '[email protected]'
Subject: RE: CC sprinklers

8.15.1.6 (07) 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Monday, July 28, 2008 8:14 AM
To: AFSA
Subject: CC sprinklers

Will someone please direct me to the section of NFPA13 2007 that covers the
circumstances requiring Tyco's CC sprinklers? I give up.

 

 

 

 

 

 

 

 

 

 

 

 

 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to