In answer to (1) use SSU/SSP Just like the old days.
Part B of (1) is a little tougher, because at some point you change from
light hazard to OH. Whenever it's OH use SSU/SSP. Just because there is
ductwork or a fan or pump, doesn't make the space OH. Do you have open flame
heating appliances, is it an OIL tank or just a well troll tank, or elect
HWH.
If per part (2) if it QUALIFIES as OH use SSU/SSP. If not use CC's. 
Most important if you use CPVC is the 1000 Sf draft stopped area, the 36"
max and 12" min. (36 and 12 apply to all types of pipe.)
One of the few places that describe what the draft stop shall do, and be.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Monday, July 28, 2008 12:53 PM
To: [email protected]
Subject: RE: CC sprinklers

This requirement is only for 2007, am I correct?

I've 2 other questions.

(1) Tyco cut sheets state this head is used for light hazard. If the area is
OH what happens? Sometimes a crawlspace is used as a mechanical room, with
tanks, pumps and other mechanical equipment.

(2) Sometimes a crawlspace is non-combustible with drywall attached to
bottom of wood joists or TJI's, but is required to be sprinklered due to
storage/mech. equipment etc. I would think 8.15.1.6 (07) should apply, but
is the wording clear? In this case, I think the 36" clearance is from floor
to ceiling (bottom of drywall) of the crawlspace. Right?

Tony 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt Willis
Sent: July 28, 2008 7:33 AM
To: [email protected]
Subject: FW: CC sprinklers

 

-----Original Message-----
From: Matt Willis
Sent: Monday, July 28, 2008 8:30 AM
To: '[email protected]'
Subject: RE: CC sprinklers

8.15.1.6 (07) 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Monday, July 28, 2008 8:14 AM
To: AFSA
Subject: CC sprinklers

Will someone please direct me to the section of NFPA13 2007 that covers the
circumstances requiring Tyco's CC sprinklers? I give up.

 

 

 

 

 

 

 

 

 

 

 

 

 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.138 / Virus Database: 270.5.6/1577 - Release Date: 7/28/2008
6:55 AM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to