In answer to (1) use SSU/SSP Just like the old days. Part B of (1) is a little tougher, because at some point you change from light hazard to OH. Whenever it's OH use SSU/SSP. Just because there is ductwork or a fan or pump, doesn't make the space OH. Do you have open flame heating appliances, is it an OIL tank or just a well troll tank, or elect HWH. If per part (2) if it QUALIFIES as OH use SSU/SSP. If not use CC's. Most important if you use CPVC is the 1000 Sf draft stopped area, the 36" max and 12" min. (36 and 12 apply to all types of pipe.) One of the few places that describe what the draft stop shall do, and be.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva Sent: Monday, July 28, 2008 12:53 PM To: [email protected] Subject: RE: CC sprinklers This requirement is only for 2007, am I correct? I've 2 other questions. (1) Tyco cut sheets state this head is used for light hazard. If the area is OH what happens? Sometimes a crawlspace is used as a mechanical room, with tanks, pumps and other mechanical equipment. (2) Sometimes a crawlspace is non-combustible with drywall attached to bottom of wood joists or TJI's, but is required to be sprinklered due to storage/mech. equipment etc. I would think 8.15.1.6 (07) should apply, but is the wording clear? In this case, I think the 36" clearance is from floor to ceiling (bottom of drywall) of the crawlspace. Right? Tony -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matt Willis Sent: July 28, 2008 7:33 AM To: [email protected] Subject: FW: CC sprinklers -----Original Message----- From: Matt Willis Sent: Monday, July 28, 2008 8:30 AM To: '[email protected]' Subject: RE: CC sprinklers 8.15.1.6 (07) -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Monday, July 28, 2008 8:14 AM To: AFSA Subject: CC sprinklers Will someone please direct me to the section of NFPA13 2007 that covers the circumstances requiring Tyco's CC sprinklers? I give up. Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - http://www.avg.com Version: 8.0.138 / Virus Database: 270.5.6/1577 - Release Date: 7/28/2008 6:55 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)