Okay, here is an actual case in design now, I'm not making this up. The
room is 27'x 27' with 2 ft. wide gap between the walls and ceiling on
three sides. Two sides have sheet rock from the ceiling to the deck. The
third side has return air grills set on edge vertically for the full 25
ft. dimension creating a 50 sqft continuous return. Do the return air
grills have any effect on the requirement for sprinklers in the plenum?

NFPA does not allow any wiggle room (IMHO) and requires sprinklers
throughout when it is not a concealed space. AHJ's have no incentive to
allow anything less than the minimum and potentially a big down side if
they do, so we always add sprinklers above the ceiling.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ



 