I did a similar project a couple of years back and the place was
insured by FM Global (except these ceiling panels were in the shape
of a wave). After much discussion, we put sprinklers both above and
below and included both sets in the design area. To my knowledge,
there is no fire data, either test or forensic, that would give a
meaningful guide for design criteria. Best to err on the side of overkill.
At 08:59 AM 8/5/2008, you wrote:
Content-Language: en-US
Content-Type: multipart/related; boundary="=_reb-r0218EB78-t48984EA5";
type="multipart/alternative"
I am in the design phase installing wet pipe sprinkler systems
protecting new schools.
I have noticed that in several of the rooms in the
schools(cafeteria, band room, main corridor that runs the length of
the school), architect has designed lay-in ceiling systems with gaps
ranging from 4" to 12" along the walls and between sections of
ceiling within the rooms (floating ceiling sections).
I do not believe my non-combustible concealed space above the
ceilings is concealed anymore and may require protection.
Has anyone dealt with this?
I have heard some discussion that if the total square feet of the
openings is below a certain percent of the total square foot of a
space, sprinkler protection above the space may not be required?
Interesting thing is that the school is being built as a "Green"
project and seems like the designed openings would make the schools
less energy efficient.
Anyone's help would be most appreciated...
Rick E. Green
District Manager
East Coast Fire Protection, Inc.
1113 Cavalier Boulevard
Chesapeake, Virginia 23323
757/485-7486(p), 757/295-0956(direct), 757/328-0131(cell)
[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)