Jim,
The design requirements for a group III hangar are in NFPA 13, I believe it is 
Extra Group II but look it up. Somewhere in the gobbledigook of NFPA 409 it 
refers you to 13 for the design requirements, but I don't remember where.
Mark

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Thiesse,
Jim
Sent: Tuesday, September 02, 2008 3:21 PM
To: [email protected]
Subject: Protection of Group 3 Aircraft Hangars


I could use some help regarding NFPA 409, specifically the design
requirements for a group 3 aircraft hangar.  

 

I found the requirements for hangar groups 1&2, but section 8.9 (FIRE
PROTECTION FOR GROUP 3 HANGARS) says:

 8.9.1*
<javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0197222',%20'',%20
'codes-id00040901511')>  Where hazardous operations, including fuel
transfer, welding, torch cutting, torch soldering, doping, and spray
painting, are performed in any Group III hangar, the Group III hangar
shall be protected with the fire protection specified in Chapter 7
<javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0196850',%20'/',%2
0'codes-id00040900688')>  and also shall meet the requirements specified
in 5.4.2
<javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0196560',%20'/',%2
0'codes-id00040900166')> . 

 

What if it's just a storage hangar and the above listed operations are
not expected?  Group 2 hangars require a .17/5,000 sq. ft.  Does that
also apply to ALL group 3 hangars?

 

In NFPA 13 under extra hazard (group 1) occupancies it lists aircraft
hangars (except as governed by NFPA 409).  I don't see any exceptions in
NFPA 409 exempting any hangars.

 

Any help would be appreciated.

 

Thanks,

Jim Thiesse

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)