What is being stored? IF it isn't airplanes, why call it a hangar?
Assuming it IS a hangar (and not a building on an air field that looks
like a duck but isn't one) and as pointed out, does not have the
hazards identified in 409 then it is not required to be sprinklered
per 409. IF something else triggers the requirement for sprinklers
THEN you go to NFPA 13 which dictates an EHG1 category.
Hopefully that extracts some of the mud from the water.
Roland
On Sep 2, 2008, at 3:21 PM, Thiesse, Jim wrote:
I could use some help regarding NFPA 409, specifically the design
requirements for a group 3 aircraft hangar.
I found the requirements for hangar groups 1&2, but section 8.9 (FIRE
PROTECTION FOR GROUP 3 HANGARS) says:
8.9.1*
<javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0197222',%20'',
%20
'codes-id00040901511')> Where hazardous operations, including fuel
transfer, welding, torch cutting, torch soldering, doping, and spray
painting, are performed in any Group III hangar, the Group III hangar
shall be protected with the fire protection specified in Chapter 7
<javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0196850',
%20'/',%2
0'codes-id00040900688')> and also shall meet the requirements
specified
in 5.4.2
<javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0196560',
%20'/',%2
0'codes-id00040900166')> .
What if it's just a storage hangar and the above listed operations are
not expected? Group 2 hangars require a .17/5,000 sq. ft. Does that
also apply to ALL group 3 hangars?
In NFPA 13 under extra hazard (group 1) occupancies it lists aircraft
hangars (except as governed by NFPA 409). I don't see any
exceptions in
NFPA 409 exempting any hangars.
Any help would be appreciated.
Thanks,
Jim Thiesse
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)