Craig, Sprinklers would be required by 101 but under the conditions discussed not by 409 with it's increased densities. 13 would instead be the guiding standard.
On Wed, Sep 3, 2008 at 1:14 PM, <[EMAIL PROTECTED]> wrote: > What type of storage does NFPA 101 not require to be sprinkled? The building > code requires sprinklers for some depending on the commodity stored. > > How can an aircraft be considered a low hazard commodity? > > > Craig L. Prahl, CET > Fire Protection Group > Mechanical Department > CH2MHILL > Lockwood Greene > 1500 International Drive > PO Box 491, Spartanburg, SC 29304-0491 > Direct - 864.599.4102 > Fax - 864.599.8439 > [EMAIL PROTECTED] > http://www.ch2m.com > > -----Original Message----- > From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fox Duane T. > (FireMarshal) > Sent: Wednesday, September 03, 2008 2:56 PM > To: [email protected] > Subject: RE: Protection of Group 3 Aircraft Hangars > > Jim, > > NFPA 409 does not require a sprinkler system (Group III Hangar) if there is > no fuel transfer, welding, torch cutting or soldering, doping, or spray > painting. The only requirement is a portable fire extinguisher in accordance > with NFPA 10. NFPA 101 does not require a storage building to be > sprinklered. If the building code requires it then you have a choice either > protect it as a Group II Hangar or use the storage criteria out of NFPA 13 > (EH-1). There should be no AHJ judgment on the demand of the system. Either > is code compliant as long as you provide coverage in accordance with all the > Group II demands for an automatic sprinkler system, or the storage > requirement demand from NFPA 13 (EH-1). > The only judgment I would use, as an AHJ, is that the hazards listed above > are truly not present. Usually, I ask for this in writing from the owner of > the hangar and the owner of the plane (if different), so when a follow up > inspection, on a complaint basis, is done and the hazards exist I can issue a > violation and make the sprinkler system mandatory. > > It is always better to get the sprinkler system installed up front. It > causes the owner of the hangar less headaches in the end and more flexibility > when leasing the space. > > Duane Fox, Jr. > DE State Fire Marshal's Office > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Thiesse, Jim > Sent: Wednesday, September 03, 2008 2:05 PM > To: [email protected] > Subject: RE: Protection of Group 3 Aircraft Hangars > > The code plan lists this as a group 3 hangar (S-2 Occupancy), and there will > definitely be aircraft stored inside, but there's no indication that the > hangar will be used for any fuel transfer, welding, torch cutting, torch > soldering, doping or spray painting, so it appears to be just an aircraft > storage hangar. > > What your saying is that a group 3 hangar meeting this criteria should be > protected using NFPA-13 EHG1, but NFPA 409 doesn't specifically tell you that > in chapter 8.9, nor does it refer you to 13 at all, so is it just a case by > case judgment call to me made by each local AHJ? > > Thanks for the help! > Jim > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins > Sent: Wednesday, September 03, 2008 7:57 AM > To: [email protected] > Subject: Re: Protection of Group 3 Aircraft Hangars > > What is being stored? IF it isn't airplanes, why call it a hangar? > > Assuming it IS a hangar (and not a building on an air field that looks like a > duck but isn't one) and as pointed out, does not have the hazards identified > in 409 then it is not required to be sprinklered per 409. IF something else > triggers the requirement for sprinklers THEN you go to NFPA 13 which dictates > an EHG1 category. > > Hopefully that extracts some of the mud from the water. > > Roland > > On Sep 2, 2008, at 3:21 PM, Thiesse, Jim wrote: > >> I could use some help regarding NFPA 409, specifically the design >> requirements for a group 3 aircraft hangar. >> >> >> >> I found the requirements for hangar groups 1&2, but section 8.9 (FIRE >> PROTECTION FOR GROUP 3 HANGARS) says: >> >> 8.9.1* >> <javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0197222',%20'', >> %20 >> 'codes-id00040901511')> Where hazardous operations, including fuel >> transfer, welding, torch cutting, torch soldering, doping, and spray >> painting, are performed in any Group III hangar, the Group III hangar >> shall be protected with the fire protection specified in Chapter 7 >> <javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0196850', >> %20'/',%2 >> 0'codes-id00040900688')> and also shall meet the requirements >> specified in 5.4.2 >> <javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0196560', >> %20'/',%2 >> 0'codes-id00040900166')> . >> >> >> >> What if it's just a storage hangar and the above listed operations are >> not expected? Group 2 hangars require a .17/5,000 sq. ft. Does that >> also apply to ALL group 3 hangars? >> >> >> >> In NFPA 13 under extra hazard (group 1) occupancies it lists aircraft >> hangars (except as governed by NFPA 409). I don't see any exceptions >> in NFPA 409 exempting any hangars. >> >> >> >> Any help would be appreciated. >> >> >> >> Thanks, >> >> Jim Thiesse >> >> _______________________________________________ >> Sprinklerforum mailing list >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> For Technical Assistance, send an email to: > [EMAIL PROTECTED] >> >> To Unsubscribe, send an email > to:[EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) >> > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: > [EMAIL PROTECTED] > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: > [EMAIL PROTECTED] > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [EMAIL PROTECTED] > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [EMAIL PROTECTED] > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)