If the water supply is a big issue but flammable liquid leaks or spills are
the hazard, FireFlex compressed air foam could be the answer. We are
completing the design for a 19000SF hanger in Columbus, OH with ICAF sold
through Viking. Fire pumps and suction tank went away with reduced water
supply required with 3% deluge foam application. Rural airports may have
water supply deficiencies that could be solved with ICAF.

Art Tiroly

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, September 03, 2008 10:57 AM
To: [email protected]
Subject: Re: Protection of Group 3 Aircraft Hangars

What is being stored?  IF it isn't airplanes, why call it a hangar?

Assuming it IS a hangar (and not a building on an air field that looks  
like a duck but isn't one) and as pointed out, does not have the  
hazards identified in 409 then it is not required to be sprinklered  
per 409.  IF something else triggers the requirement for sprinklers  
THEN you go to NFPA 13 which dictates an EHG1 category.

Hopefully that extracts some of the mud from the water.

Roland

On Sep 2, 2008, at 3:21 PM, Thiesse, Jim wrote:

> I could use some help regarding NFPA 409, specifically the design
> requirements for a group 3 aircraft hangar.
>
>
>
> I found the requirements for hangar groups 1&2, but section 8.9 (FIRE
> PROTECTION FOR GROUP 3 HANGARS) says:
>
> 8.9.1*
> <javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0197222',%20'', 
> %20
> 'codes-id00040901511')>  Where hazardous operations, including fuel
> transfer, welding, torch cutting, torch soldering, doping, and spray
> painting, are performed in any Group III hangar, the Group III hangar
> shall be protected with the fire protection specified in Chapter 7
> <javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0196850', 
> %20'/',%2
> 0'codes-id00040900688')>  and also shall meet the requirements  
> specified
> in 5.4.2
> <javascript:parent.loadDoc('/nfpa0400-0499/0409/codes-0196560', 
> %20'/',%2
> 0'codes-id00040900166')> .
>
>
>
> What if it's just a storage hangar and the above listed operations are
> not expected?  Group 2 hangars require a .17/5,000 sq. ft.  Does that
> also apply to ALL group 3 hangars?
>
>
>
> In NFPA 13 under extra hazard (group 1) occupancies it lists aircraft
> hangars (except as governed by NFPA 409).  I don't see any  
> exceptions in
> NFPA 409 exempting any hangars.
>
>
>
> Any help would be appreciated.
>
>
>
> Thanks,
>
> Jim Thiesse
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to