Thom,
What makes me worry is that we say FM-200 gas is safe for occupied spaces & 
will not affect the personnels in the computer room.
Imagin that the volume of cabinets is about 25% of total volume, so if my 
design concentration is 7.4% then the real concentration is 9.25%.
I agree that cabinets are not "Gas Tight" and will become filled with the FM200 
just
at a slower rate, but it takes time, may be for 2 minutes, then can we still 
say this gas is safe while the personnels may be subjected to 9.62% even at the 
first 2 minutes of gas release?
 
Thanks,
Reza
 
 
 
Short answer NO!

The cabinets are not "Gas Tight" and will become filled with the FM200 just
at a slower rate, than the rest of the room.