Craig:

You're ignoring the fact that Clean Agent systems almost never discharge during 
a true 'fire' scenario.  Detection will identify a fire long before open flames 
occur, so it is highly unlikely that anyone may be 'going down with the ship.'  
And if you consider the use of fluids like NOVEC, what is the problem? They're 
designed to discharge concentrations below 6%, and have no observable adverse 
affects at or below 10%.  In fact, they don't know when the adverse affects 
occur - just not at or below 10%.  When the system discharges, it suppresses a 
fire, so again, what ship is going down?

Now, it is generally good practice to get out of the room during the 30 sec. 
warning period. But what do you do if you're a 911 operator taking a call?

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, September 03, 2008 2:41 PM
To: [email protected]
Subject: RE: FM-200 enclosure volume (Exclude Cabinets volume?)

If in fact it is a requirement by the employer/owner that personnel remain in 
the room when a system discharges someone needs their head examined.

If the system is in discharge mode it is likely there is a fire scenario 
occurring, what imbecile would require his employees to "go down with the ship"?

If in the U.S. this has to violate not only most corporate safety standards but 
probably a few OSHA standards as well.  Rally the lawyers boys it's feedin' 
time!

For countries where personnel safety is of no concern it might be different.

But if this is a major concern then it would be best to look toward another 
extinguishing method other than gas, water mist or even pre-action sprinklers 
would be better.





Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reed Roisum
Sent: Wednesday, September 03, 2008 3:28 PM
To: '[email protected]'
Subject: RE: FM-200 enclosure volume (Exclude Cabinets volume?)

Each of the clean agent gases have a NOAEL (No Observable Adverse Effect Level) 
number that they have been tested to.  For example, the NOAEL % for Novec 1230 
is 10%, (this means that they have exposed an animal to that concentration with 
no observable adverse effects) and the design concentration for Class A Hazards 
is 4.2%.

FM-200 has a 9% NOAEL and approximately a 7% design concentration for Class A 
Hazards.  So, the safety margin is not as wide and so there is less flexibility 
when adding cabinets etc. that would change the volume and consequently change 
the concentration.


Reza is right to be concerned about personnel occupying an area during 
discharge.  I have heard of applications where the personnel are required to 
stay in the space during discharge and the design of the clean agent system 
needs to allow for that possibility.

I would talk to an FM-200 supplier who does the actual design to find out what 
they include in the volume calculations.  Personally, I was told to not include 
the volume of server racks etc., but I would be inclined to include the volume 
of the cabinets depending how easily the gas can get in and fill the volume.

Reed A. Roisum, CET
Fire Protection Technician

Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079

Direct Number: 701.280.8580
Mobile: 701.212.8810
Main Office: 701.280.8500

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili
Sent: Wednesday, September 03, 2008 1:06 PM
To: [email protected]
Subject: RE: FM-200 enclosure volume (Exclude Cabinets volume?)

Thom,
What makes me worry is that we say FM-200 gas is safe for occupied spaces & 
will not affect the personnels in the computer room.
Imagin that the volume of cabinets is about 25% of total volume, so if my 
design concentration is 7.4% then the real concentration is 9.25%.
I agree that cabinets are not "Gas Tight" and will become filled with the FM200 
just at a slower rate, but it takes time, may be for 2 minutes, then can we 
still say this gas is safe while the personnels may be subjected to 9.62% even 
at the first 2 minutes of gas release?

Thanks,
Reza



Short answer NO!

The cabinets are not "Gas Tight" and will become filled with the FM200 just at 
a slower rate, than the rest of the room.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to