If you don't count the cabinet space and it was 25% of the volume of the room, then at some point your concentration will be too low to extinguish the fire, so how did you save your client money? There all kinds of what if's. We use the volume of the room, and then seal that volume, for a reason. It's the only way to contain the gas, and maintain the concentration level.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Wednesday, September 03, 2008 12:06 PM To: [email protected] Subject: RE: FM-200 enclosure volume (Exclude Cabinets volume?) Thom, What makes me worry is that we say FM-200 gas is safe for occupied spaces & will not affect the personnels in the computer room. Imagin that the volume of cabinets is about 25% of total volume, so if my design concentration is 7.4% then the real concentration is 9.25%. I agree that cabinets are not "Gas Tight" and will become filled with the FM200 just at a slower rate, but it takes time, may be for 2 minutes, then can we still say this gas is safe while the personnels may be subjected to 9.62% even at the first 2 minutes of gas release? Thanks, Reza Short answer NO! The cabinets are not "Gas Tight" and will become filled with the FM200 just at a slower rate, than the rest of the room. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)