Hello Reza, and if one of the cabinet doors is open when the system discharges it will fill faster... How about a fourth of the doors open when it discharges with your concentration of 7.4% then you have diluted below that.
Wednesday, September 3, 2008, 2:05:33 PM, you wrote: > Thom, > What makes me worry is that we say FM-200 gas is safe for occupied > spaces & will not affect the personnels in the computer room. > Imagin that the volume of cabinets is about 25% of total volume, so if > my design concentration is 7.4% then the real concentration is 9.25%. > I agree that cabinets are not "Gas Tight" and will become filled with the > FM200 just > at a slower rate, but it takes time, may be for 2 minutes, then can we > still say this gas is safe while the personnels may be subjected to 9.62% > even at the first 2 minutes of gas release? > > Thanks, > Reza > > > > Short answer NO! > The cabinets are not "Gas Tight" and will become filled with the FM200 just > at a slower rate, than the rest of the room. > Thom McMahon, SET > Firetech, Inc. > 2560 Copper Ridge Dr > P.O. Box 882136 > Steamboat Springs, CO 80488 > Tel: > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [EMAIL PROTECTED] > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) -- Best regards, Charles Thurston mailto:[EMAIL PROTECTED] Coastal Fire Protection _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)