Hello Reza,

and if one of the cabinet doors is open when the system discharges it will
fill faster...  How about a fourth of the doors open when it discharges
with your concentration of 7.4% then you have diluted below that.

Wednesday, September 3, 2008, 2:05:33 PM, you wrote:

> Thom,
> What makes me worry is that we say FM-200 gas is safe for occupied
> spaces & will not affect the personnels in the computer room.
> Imagin that the volume of cabinets is about 25% of total volume, so if
> my design concentration is 7.4% then the real concentration is 9.25%.
> I agree that cabinets are not "Gas Tight" and will become filled with the 
> FM200 just
> at a slower rate, but it takes time, may be for 2 minutes, then can we
> still say this gas is safe while the personnels may be subjected to 9.62%
> even at the first 2 minutes of gas release?
>  
> Thanks,
> Reza
>  
>  
>  
> Short answer NO!

> The cabinets are not "Gas Tight" and will become filled with the FM200 just
> at a slower rate, than the rest of the room.

> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  


>       
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]

> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)



-- 
Best regards,
 Charles Thurston                            mailto:[EMAIL PROTECTED]
  Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to