The Tyco limitations are because that is what is required to keep the
glass intact, make the sprinkler work properly, and ensure the wall
rating.  If it is designed, installed, approved, and accepted
incorrectly it is still wrong regardless of what the AHJ approves. With
all due respect Ron, you won't be okay if something goes wrong and you
haven't used the Tyco sprinkler given that it is available for this
specific application and the information in the thread below including
Chris' input.

Scott   

(763) 425-1001 Office 
(612) 759-5556 Cell 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, September 30, 2008 7:59 AM
To: [email protected]
Subject: RE: Window Sprinklers

If the AHJ will approve closely spaced sprinklers you should be okay.
The Tyco window sprinkler has some severe limitations like no horizontal
mullions which translates to no doors.

Just because a sprinkler is UL Listed for an application it doesn't mean
it's the only thing that can be used. We at the office have often
discussed submitting a line of sprinklers to UL for testing and sending
along a tanker truck of water from phoenix for the test. We would then
have the only sprinkler UL Listed with Phoenix water. Following the
window sprinkler logic everyone would have to buy our sprinkler if they
did work in Phoenix. (lol)

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Tuesday, September 30, 2008 5:21 AM
To: AFSA
Subject: Window Sprinklers

Mornin'. I am bidding a project which consists of an educational
facility.
Down the center of the building runs an 8' wide corridor. 60' of one of
the
corridor walls is glass. The corridor walls are fire rated so I am
installing sprinklers on both sides of the glass at a max. of  6'
spacing.
Tyco makes a sprinkler expressly for this use. I can find nothing in
codes
or standards that require me to use this Tyco sprinkler. Does anyone
know of
a requirement to use this sprinkler? Why would a contractor choose to
use an
$80.00 Tyco sprinkler when a $3.00 SSP will do the same job? This makes
me
concerned that there is one sorta like the CC1 and CC2 sprinkler.

Any input will be greatly appreciated.



 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to