A smart architect would have known there are limitations on windows and glazing 
in rated construction.   He should have been asking some questions before just 
"drawing up a drawing" and saying "make it so".


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, September 30, 2008 9:55 AM
To: [email protected]
Subject: RE: Window Sprinklers

It's permitted this way so what's a fellow to do? Tell the Architect/Engineer, 
Building Department, Fire Department and owner that they have to eliminate the 
doors and horizontal mullions from 80 ft. of glass wall? And by the way, the 
next time you want to use a glass wall you have to check with Tyco?

By the time we find out about the rated glass wall all the permits are issued 
and construction has begun. It's probably a little too late to architecturally 
redesign the entire lobby area.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Scott A.
Futrell
Sent: Tuesday, September 30, 2008 6:16 AM
To: [email protected]
Subject: RE: Window Sprinklers

The Tyco limitations are because that is what is required to keep the glass 
intact, make the sprinkler work properly, and ensure the wall rating.  If it is 
designed, installed, approved, and accepted incorrectly it is still wrong 
regardless of what the AHJ approves. With all due respect Ron, you won't be 
okay if something goes wrong and you haven't used the Tyco sprinkler given that 
it is available for this specific application and the information in the thread 
below including Chris' input.

Scott

(763) 425-1001 Office
(612) 759-5556 Cell


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, September 30, 2008 7:59 AM
To: [email protected]
Subject: RE: Window Sprinklers

If the AHJ will approve closely spaced sprinklers you should be okay.
The Tyco window sprinkler has some severe limitations like no horizontal 
mullions which translates to no doors.

Just because a sprinkler is UL Listed for an application it doesn't mean it's 
the only thing that can be used. We at the office have often discussed 
submitting a line of sprinklers to UL for testing and sending along a tanker 
truck of water from phoenix for the test. We would then have the only sprinkler 
UL Listed with Phoenix water. Following the window sprinkler logic everyone 
would have to buy our sprinkler if they did work in Phoenix. (lol)

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Tuesday, September 30, 2008 5:21 AM
To: AFSA
Subject: Window Sprinklers

Mornin'. I am bidding a project which consists of an educational facility.
Down the center of the building runs an 8' wide corridor. 60' of one of the 
corridor walls is glass. The corridor walls are fire rated so I am installing 
sprinklers on both sides of the glass at a max. of  6'
spacing.
Tyco makes a sprinkler expressly for this use. I can find nothing in codes or 
standards that require me to use this Tyco sprinkler. Does anyone know of a 
requirement to use this sprinkler? Why would a contractor choose to use an 
$80.00 Tyco sprinkler when a $3.00 SSP will do the same job? This makes me 
concerned that there is one sorta like the CC1 and CC2 sprinkler.

Any input will be greatly appreciated.





Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to