Are they going to store all of the haunted house stuff in there during the off season? If so, then you have a storage occupancy, which would provide an exposure to a grandstand, especially when occupied. Doesn't sound like a good idea. Does Nebraska law allow sprinkler systems with no permanent water supply? Try NFPA 13 (2002) section 15.1.1.


At 10:30 AM 9/30/2008, you wrote:
"A smart architect.........."

That's pretty funny for a Tuesday morning.


This question is for the AHJ's or anybody that what to chime in.

We have a Haunted House that wants to build under a grandstand of a local dirt-track. Per the code it needs to be sprinkler protected. Since this area is subject to freezing; they want to install what I would call a manual dry-pipe system. The system would have no water supply, just a FDC with a pumper attached when the "house" is occupied.
If the hydraulics work out, anyone see anything wrong with this scenario?


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Tuesday, September 30, 2008 9:08 AM
To: [email protected]
Subject: RE: Window Sprinklers

A smart architect would have known there are limitations on windows and glazing in rated construction. He should have been asking some questions before just "drawing up a drawing" and saying "make it so".


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, September 30, 2008 9:55 AM
To: [email protected]
Subject: RE: Window Sprinklers

It's permitted this way so what's a fellow to do? Tell the Architect/Engineer, Building Department, Fire Department and owner that they have to eliminate the doors and horizontal mullions from 80 ft. of glass wall? And by the way, the next time you want to use a glass wall you have to check with Tyco?

By the time we find out about the rated glass wall all the permits are issued and construction has begun. It's probably a little too late to architecturally redesign the entire lobby area.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Scott A.
Futrell
Sent: Tuesday, September 30, 2008 6:16 AM
To: [email protected]
Subject: RE: Window Sprinklers

The Tyco limitations are because that is what is required to keep the glass intact, make the sprinkler work properly, and ensure the wall rating. If it is designed, installed, approved, and accepted incorrectly it is still wrong regardless of what the AHJ approves. With all due respect Ron, you won't be okay if something goes wrong and you haven't used the Tyco sprinkler given that it is available for this specific application and the information in the thread below including Chris' input.

Scott

(763) 425-1001 Office
(612) 759-5556 Cell


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, September 30, 2008 7:59 AM
To: [email protected]
Subject: RE: Window Sprinklers

If the AHJ will approve closely spaced sprinklers you should be okay.
The Tyco window sprinkler has some severe limitations like no horizontal mullions which translates to no doors.

Just because a sprinkler is UL Listed for an application it doesn't mean it's the only thing that can be used. We at the office have often discussed submitting a line of sprinklers to UL for testing and sending along a tanker truck of water from phoenix for the test. We would then have the only sprinkler UL Listed with Phoenix water. Following the window sprinkler logic everyone would have to buy our sprinkler if they did work in Phoenix. (lol)

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Tuesday, September 30, 2008 5:21 AM
To: AFSA
Subject: Window Sprinklers

Mornin'. I am bidding a project which consists of an educational facility.
Down the center of the building runs an 8' wide corridor. 60' of one of the corridor walls is glass. The corridor walls are fire rated so I am installing sprinklers on both sides of the glass at a max. of 6'
spacing.
Tyco makes a sprinkler expressly for this use. I can find nothing in codes or standards that require me to use this Tyco sprinkler. Does anyone know of a requirement to use this sprinkler? Why would a contractor choose to use an $80.00 Tyco sprinkler when a $3.00 SSP will do the same job? This makes me concerned that there is one sorta like the CC1 and CC2 sprinkler.

Any input will be greatly appreciated.





Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) _______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________