The formula I have is; Q=29.83*cd2*sqrt of pitot pressure.
29.83*(5.625)*7.41 Q=1243.35 John Drucker Fire Protection Subcode Official Borough of Red Bank, NJ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Timothy W Goins Sent: Tuesday, October 14, 2008 10:32 PM To: [email protected] Subject: RE: FLOW / PITOT READINGS If your pitot pressure is 25.0615 psi it is. (c=.90) -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Forest Wilson Sent: Tuesday, October 14, 2008 8:43 PM To: [email protected] Subject: FLOW / PITOT READINGS Am I ignorant on this subject? Please let me know. If you flow a 2 1/2" hydrant, and the pitot reading is 55 psi the gpm will always be 1250. Right? (I understand you factor in the coefficient of the hydrant nozzle). My pitot gauge manufac tured by Potter shows BOTH gpm AND psi. I'm looking at a flow test paper. Through a 2.5" hydrant outlet. Residual is 90 psi @ 840 GPM. Is this possible? Forest Wilson Cherokee Fire Pro. a _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)