Tom,

Do you know why the Pollards are in accurate? I have read that there is
problem with the pitot being inside a short tube.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Wednesday, October 15, 2008 5:55 AM
To: [email protected]
Subject: RE: FLOW / PITOT READINGS

What Steve said plus get rid of that pollard diffuser, very inaccurate.
Use a couple of playpipes if you don't have a monster.

Tom


A pitot measures velocity pressure, which is converted to flow in GPM
per the formula already posted by others.  Residual is the pressure left
in the main when it is flowing a fixed amont of water, such as might be
measured with a pitot.  See NFPA 291; in the standard 2 hydrant flow
test, the pitot and residual are measured at separate hydrants.   