How much higher are the tank discharge flanges above the pump suction
flange?

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of A.P.Silva
> Sent: Friday, October 31, 2008 11:32 AM
> To: [email protected]
> Subject: Fire Pump Suction
> 
> 
> 400 gpm fire pump supplied from tanks with suction flanges higher than
> pump
> suction flange. Approximately 100 feet of 4" piping (including fittings)
> from tanks to pump. NFPA 20 permits the gauge pressure at the pump
> suction
> flange to drop to -3 psi, with the pump flowing at 150% (600 gpm in this
> case). The friction loss in the piping for 600 gpm flow is about 7.6
> psi. Is
> there a concern for the pressure available at the pump suction, when the
> water level drops in the tanks? I have been told that it will, so
> checking
> the opinion of the forum.
> 
> Tony
> 