Ed-
I'd agree that the choice is yours in #22.

I don't have time to jump into #20, but it could be the auto part is
required is you're counting on a smaller than minimum design capacity tank
and the refill is counted as part of the duration- since obviously that
would have to be an auto fill. 

This isn't an opinion of the NFPA #22 Committee, just that of the writer.

George Church
Rowe Sprinkler

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Wednesday, November 19, 2008 1:28 AM
To: [email protected]
Subject: Storage tank fill line

Is an underground storage tank (designed per NFPA 22) required to have an
automatic fill line (as opposed to a manual fill line)?  In this case, the
tank supplies a vertical turbine fire pump that supplies a sprinkler system.

 

Section 5.6.4.1 of NFPA 20 (07) says "A stored supply plus reliable
automatic refill shall be sufficient to meet the demand placed upon it for
the design duration."  OK, but I'm not finding anything that says the refill
is required to be automatic.    

 

Jump to NFPA 22 (03).  Section 13.4 addresses filling of the tank.  Section
13.4.6 addresses filling of suction tanks and talks about where an automatic
fill line must connect to the tank, but doesn't say an automatic fill is
required.  Section 13.4.1.4 says the control valve on a bypass loop used to
fill a tank shall be kept closed except when the tank is being filled.
Sounds manual to me.

 

So all this leads me to believe the fill line is allowed to be manual or
automatic (designer's choice).   Or am I missing something?

 

Ed Kramer

Littleton, CO

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to